For turbulent (sprinkler) flows, friction loss is proportional to the square
of the velocity

-----Original Message-----
From: Matt Grise [mailto:[email protected]] 
Sent: Tuesday, June 15, 2010 12:41 PM
To: '[email protected]'; '[email protected]'
Subject: RE: Gravity Tanks

Don't forget friction in the pipes!

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Tuesday, June 15, 2010 12:39 PM
To: [email protected]; [email protected]
Subject: RE: Gravity Tanks

i.e., if the water level is 280 feet 'above your head', then h=280 ft, v=134
ft/sec (same as the Law of Falling Bodies- if you were dropped from 280 ft,
you would be going 134 ft/sec when you hit the ground).
ft/sec*ft^2=ft^3/sec. If the flow is coming out of 4" pipe, ft^2=.09----
*134= 12 * 7.48= 90---- * 60= 5400 GPM. As the level 'above your head'
drops, so does the velocity, so either use calculus, or call h the bottom of
the tank, like I would have to do. It still seems like magic to me that by
just using feet and seconds, given the rated psi and rpm ONLY, of a fire
pump, I can calculate the diameter of the impeller (v=2*pi*r*f). It seems
like magic bcoz for 15 years I tried to learn sprinkler calcs after the PEs
had simplified it enough for me by factoring gravity out of the formulas.   

-----Original Message-----
From: Brad [mailto:[email protected]] 
Sent: Tuesday, June 15, 2010 8:30 AM
To: [email protected]
Subject: RE: Gravity Tanks

mgh=.5mv^2
m is the same on both sides so 
v= sq root 2gh
h= v^2/2g
first thing is forget about gallons, minutes, and psi- use feet and seconds:
ft, ft^2, ft^3, sec, sec^2. ft/sec=(ft^3/sec)/ft^2)
g=32.2 ft/sec^2 (if this project is on the earth). 7.48 gal/ft^3. water
weighs 62.4 lbs/ft^3.

-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Tuesday, June 15, 2010 5:11 AM
To: [email protected]
Subject: Gravity Tanks

Was there a thread on calculating flow from a gravity tanks a while 
back? I couldn't find it. I have to do a calculation on the first 
floor of a building fed from a gravity tank on the 28th floor

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to