In the 2007 of 13, the rules for the room design method were 
modified. There is now language which states "or when extended 
coverage sprinklers are installed, all sprinklers within 75 linear 
feet of the corridor". Does this imply that fewer than 5 may be 
calculated (i.e 4 sprinklers at 20'). If you have a mix of standard 
and extended coverage sprinklers in a corridor (standard in the 
corridor and xcov at the 16x16 corridor junction), that we have to 
expand the area out to the 75ft?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT