Forest, Please note the first of my post where I stated "if an older system is being upgraded".In most cases,when there is new ownership requireing a system upgrade then you also may be looking at a change in occupancy.That may be negotiable depending on the change and certainly today with the economy in it's present state. Also,unreasonable or not,in these parts,new ownership requires new C.O. which ultimately requires ALL systems to be inspected and acceptable by todays standards.
Lamar Vaughn,SET Vaughn and Company McDonough,Ga. 678-429-3563 ---- "[email protected]" <[email protected]> wrote: > ----- Forwarded message ----- From: "[email protected]" <[email protected]> Date: Tue, Jul 6, 2010 3:53 pm Subject: Re: Replacing 3/4" line segments To: "Loren Johnson" <[email protected]> The AHJ policy is unreasonable. You reference change in ownership requiring upgrade to a system meeting modern codes. Would this AHJ require a tenant fit out at a mall to result in a new system for the entire mall? Does he also require electrical, hvac and environmental insulation standards to be enforced even for a mere change in ownership? It would be cheaper to buy new than upgrade for such a policy. NFPA 13 requires a minimum 1" pipe size, with some special exceptions. This standard would apply to systems being renovated, such as a tenant change out requiring modification of the sprinkler system. But adding a sprinkler in an office does not mean changing all the 3/4 pipe in a warehouse. Forest Wilson Cherokee Fire Sent from my Verizon Wireless Phone ----- Reply message ----- From: "Loren Johnson" <[email protected]> Date: Tue, Jul 6, 2010 3:22 pm Subject: Replacing 3/4" line segments To: <[email protected]> While holding the posiiton of Corporate Fire Systems Engineer of a major corporation (since retired), I have followed the same guidelines for a lot of years and have never had a problem with customers, engineers, AHJs., FM Global, etc. Loren Johnson - CFPS, CET The Hitchcock Company Peoria, IL --- On Tue, 7/6/10, [email protected] <[email protected]> wrote: > From: [email protected] <[email protected]> > Subject: Re: Replacing 3/4" line segments > To: [email protected] > Date: Tuesday, July 6, 2010, 1:33 PM > I have always been instructed by > AHJ's in this area that if an older system is being upgraded > (due to a change in occupancy,ownership,or major renovation) > that the system must be brought up to current > standards.Therefore,3/4" pipe is no longer allowed. > I sure have replaced a lot of 3/4" pipe , I hope not in > error. > > Lamar Vaughn,SET > > > ---- Todd Williams <[email protected]> > wrote: > > There is nothing that says it specifically. If > > the 3/4" pipe is in good condition and the > > hydraulics support it, it can remain (unless that > > has changed post 2002). Usually I require an > > internal inspection. If it has to be modified, > > then it needs to be changed to 1" > > > > > > > > At 12:03 PM 7/6/2010, you wrote: > > >Hello, > > > > > > > > > > > >We all know that any remaining 3/4" branch lines > should be replaced with 1". > > >Where does it actually say that this must be done? > I could not find any > > >direct reference in NFPA 13 or 25. > > > > > > > > > > > >Thanks, > > > > > > > > > > > >David Bitton, Eng. > > > > > >Quest Loss Control Services Inc. > > > > > >Les services de prévention des sinistres Quest > inc. > > > > > >5100, rue de la Savane, bureau 200 > > > > > >Montréal, QC H4P 1T8 > > > > > >(514) 341-4545 > > > > > >www.questlosscontrol.com > > > > > > > > > > > >_______________________________________________ > > >Sprinklerforum mailing list > > >[email protected] > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > >For Technical Assistance, send an email to: [email protected] > > > > > >To Unsubscribe, send an email to:[email protected] > > >(Put the word unsubscribe in the subject field) > > > > Todd G. Williams, PE > > Fire Protection Design/Consulting > > Stonington, CT > > 860.535.2080 > > www.fpdc.com > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email to:[email protected] > > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)