Hii

I am facing exactly the same pblm..
We are using NFPA 30 only. but no clear cut answers
Even I am not sure whether  there is a need for any type of protection.But
unfortunatley no AHJ requirments here.
As its an open area, I presume we cant use foam sprinkler system as no
containment option  is there.

For sprinkler system Going by the higher side < I can settle down for ESFR

Am I right?





On Mon, Jul 12, 2010 at 11:22 PM, <[email protected]> wrote:

> You're dealing with many different issues but overall, an open shed if
> often not required to even have sprinklers.  I know we like to put
> sprinklers on everything but there are just times when there is no Code
> direction to do so regardless of what we think should be done.  So if
> there's no Code, AHJ or Underwriter  requirement to do so then you've got no
> way to justify it and the owner isn't going to just volunteer funds to
> protect something that's not required to be protected.  End of story, go to
> the lake and drown some worms, your work is over.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
>  From: [email protected] [mailto:
> [email protected]] On Behalf Of Todd Williams
> Sent: Monday, July 12, 2010 3:13 PM
> To: [email protected]
> Subject: RE: Flammable Liquid storage in open sheds
>
> OK. The last shed structure I dealt with was next to the water where
> wind could be an issue. However, a shed without walls, I would think,
> have very different burn characteristics than an enclosed space. The
> structure is more like a giant ceiling cloud that a room. Are you
> going to get a significant flow of fresh air at floor (or fire) level
> to replace the hot air escaping all sides around the roof? If this
> going to increase the intensity of the burn? Haven't done any
> research, but those are just questions.
>
>
>
> At 02:56 PM 7/12/2010, you wrote:
> >Todd, if a drum goes up, there'd have to be a heckuva wind to not have the
> >sprinklers activate- even by radiant heat.
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Todd
> Williams
> >Sent: Monday, July 12, 2010 2:45 PM
> >To: [email protected]
> >Subject: RE: Flammable Liquid storage in open sheds
> >
> >And since the building has no walls, how is wind going to factor in?
> >
> >
> >
> >At 02:30 PM 7/12/2010, you wrote:
> > >And then there's that ever elusive, non-conforming to anything, type of
> > >storage container that so often pops up.  Chemical storage is one of
> > >the most aggravating things I have to deal with.  Everyone expects
> > >cookie-cutter answers.  Yeah, I wish.  Then there's the chase your tail
> > >in a circle Code search for containment that can confuse the daylights
> > >out of people.
> > >
> > >Craig L. Prahl, CET
> > >Fire Protection Specialist
> > >Mechanical Department
> > >CH2MHILL
> > >Lockwood Greene
> > >1500 International Drive
> > >Spartanburg, SC  29304-0491
> > >Direct - 864.599.4102
> > >Fax - 864.599.8439
> > >[email protected]
> > >http://www.ch2m.com
> > >
> > >
> > >-----Original Message-----
> > >From: [email protected]
> > >[mailto:[email protected]] On Behalf Of George
> > >Church
> > >Sent: Monday, July 12, 2010 2:30 PM
> > >To: [email protected]
> > >Subject: RE: Flammable Liquid storage in open sheds
> > >
> > >and just when you think you've tracked down all the questions, you open
> > >up NFPA 30 and then the phone, "relieving or non-relieving?"
> > >
> > >NFPA 30 has been given to us to add back the fun we used to have with
> > >231C, which many of us don't get to experience as much with the
> > >popularity of ESFRs.
> > >I loved asking aisle widths for a spec whse, knowing the answer.
> > >
> > >glc
> > >
> > >-----Original Message-----
> > >From: [email protected]
> > >[mailto:[email protected]] On Behalf Of
> > >[email protected]
> > >Sent: Monday, July 12, 2010 2:09 PM
> > >To: [email protected]
> > >Subject: RE: Flammable Liquid storage in open sheds
> > >
> > >There are a lot of variables that need to be known before answering a
> > >question like that.
> > >
> > >Depending on what building or fire code applies the answers can vary,
> > >also the location of the shed with respect to exposure of other
> > >buildings or public ways can factor in and in a lot of cases with a
> > >Class III combustible, there may not be any need whatsoever for any
> > >kind of fixed fire protection.  There needs to be some code research
> > >performed and you need to know what the material is.  You can spray all
> > >the water you want on certain types of combustible liquids and
> > >accomplish nothing, you may need foam or foam-water.
> > >
> > >Too many unknowns here.
> > >
> > >Craig L. Prahl, CET
> > >Fire Protection Specialist
> > >Mechanical Department
> > >CH2MHILL
> > >Lockwood Greene
> > >1500 International Drive
> > >Spartanburg, SC  29304-0491
> > >Direct - 864.599.4102
> > >Fax - 864.599.8439
> > >[email protected]
> > >http://www.ch2m.com
> > >
> > >-----Original Message-----
> > >From: [email protected]
> > >[mailto:[email protected]] On Behalf Of sam b
> > >Sent: Monday, July 12, 2010 1:56 PM
> > >To: [email protected]
> > >Subject: Flammable Liquid storage in open sheds
> > >
> > >Hii..
> > >
> > >Need some help
> > >
> > >Storage:in drums
> > >Flammaeble liquid: Class III
> > >Rack storage up to max 5 m.
> > >Open shed storage with no walls (max height of shed is 7 m at eave) .
> > >
> > >
> > >Can i know what sort of protection I need to provide(Sprinkler
> > >system?). I checked NFPA 30 .but couldnt  find the exact thing.
> > >
> > >I think chapter 15,NFPA2008 edition suits the scenario. But what sort
> > >of protection and design density to consider.
> > >
> > >Can anyone give me a quick answer.?
> > >
> > >Thaanks in advance
> > >
> > >Regards
> > >Sam
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]<to%[email protected]>
> > >(Put the word unsubscribe in the subject field)
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]<to%[email protected]>
> > >(Put the word unsubscribe in the subject field)
> > >
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]<to%[email protected]>
> > >(Put the word unsubscribe in the subject field)
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email
> > >to:[email protected]<to%[email protected]>
> > >(Put the word unsubscribe in the subject field)
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email 
> >to:[email protected]<to%[email protected]>
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email 
> >to:[email protected]<to%[email protected]>
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to