Thanks, Ken.

Ed

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of ParsleyConsulting
> Sent: Thursday, July 22, 2010 11:43 AM
> To: [email protected]
> Subject: Re: 6' min spacing on sloped ceilings
> 
> Ed,
> 
> Measure on the slope.  See Figures 8.6.4.1.3.1(a) and (b) in the '10
> edition, and note the S dimension in the section.  It could be the L
> dimension if your branch lines are running perp to the slope.
> --
> 
> PARSLEY CONSULTING
> 
> Ken Wagoner, SET
> 
> 760.745.6181 voice
> 
> 760.745.0537 fax
> 
> [email protected] <mailto:[email protected]> e-mail
> 
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> 
> 
> 
> 
> Ed Kramer wrote:
> > I think I know this, but need verification.  Minimum spacing between
> SSU's
> > and SSP's is 6'.
> >
> > If installed on a sloped ceiling/roof, is the 6' a horizontal
> dimension, or
> > is it measured along the slope?
> >
> >
> >
> > Under a steeply sloped ceiling, it would be impossible to maintain 6'
> > horizontally, so I assume the intent is to measure it along the slope.
> >
> > Comments, anyone?
> >
> >
> >
> > Ed Kramer
> >
> > Littleton, CO
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> > (Put the word unsubscribe in the subject field)
> >
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to