What we see more often is a knee brace with the pipe mounted on top and a
"U" bolt to hold it in place. Similar to TOLCO fig. 31-M and 31-O. In
concrete construction the anchors in the concrete are often the weak link.
The load is both shear and pull out. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Parsley
Consulting
Sent: Friday, July 30, 2010 6:49 AM
To: [email protected]
Subject: Re: Earthquake Bracing

John,

It would seem to meet the letter of the standard in section 9.3.5.3.9.  
Do you see something there that gives you some concern about omitting 
lateral bracing?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website

IMPORTANT NOTICE: This correspondence is not a Formal
Interpretation issued pursuant to NFPA Regulations. Any opinion
expressed is the personal opinion of the author and does not necessarily
represent the official position of the NFPA or its Technical Committees.
In addition, this correspondence is neither intended, nor should it be

relied upon, to provide professional consultation or services.





John Reilly wrote:
> Please offer an opinion on bracing 6" sched. 10 main to a concrete wall.
> The method of attachment is a knee brace with a short rod and ring so that
> lateral bracing is not required.
>
> For the record, this is not my design.
>
> J. Reilly
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> ------------------------------------------------------------------------
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com 
> Version: 8.5.441 / Virus Database: 271.1.1/3037 - Release Date: 07/29/10
18:34:00
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to