Brian, the confusion and what we're all "used to" likely stems from major
HPR carriers requiring galv for dry and preaction systems over and above the
minimum concensus standards.
So #13 does NOT require the use of galv pipe in dry and preaction, but FM
Global and others will for their insured.
I'd imagine we're not the only contractor to also make it our std operating
procedure to use galv for these, too- you often end up using galv on a dry
to get the C=120 back and make the calcs work. Where it may not matter, and
if we know $ are critical, we will explain we would recommend galv but if
they want black, they can have it. I ask deelopers if this is something they
intend to lease out and then flip, or will they pass it along to their kids
as part of the family portfolio.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Monday, August 02, 2010 5:24 PM
To: [email protected]
Subject: Re: Galvanized Pipe

8.4.7 is the section for CMSA sprinklers.  Therefore 8.4.7.2.1 is only
applying to sections with CMSA sprinklers.  Is that what you are looking
for??

On 8/2/2010 2:21 PM, Brian Harris wrote:
> Had a discussion here at he office today about whether galvanize pipe 
> was required on pre-action&  dry pipe systems.... I see that 8.4.7.2.1 
> in the code book says that all steel pipe has to be internally 
> galvanized but in the handbook it elaborates a little more and says 
> that requirement is only for large drop sprinklers. Where did this 
> "extra" tidbit of information in the handbook come from?
>
>
> Brian Harris
>
>
>
>
>
>
> Design Engineer
>
>
>
> First Defense Fire Protection
> 11957 Ramah Church Road
> Huntersville NC 28078
>
>
>
>
> [email protected]
> www.firstdefensefire.com<outbind://80/www.firstdefensefire.com>
>
>
>
> Ph: 704.948.3506
> Fax: 704.948.3507
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to