Is the new fire pump to be adequate to supply the sprinkler demand only or will 
it also serve as an automatic standpipe water supply?

Lamar Vaughn,SET


---- "Johnson wrote: 
> One more piece of information.  A fire pump is scheduled to be installed as 
> part of the project.
> 
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Support Contractor)
> Office of Research Services 
> National Institutes of Health 
> 301-496-0487
> 
> 
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C] 
> Sent: Tuesday, August 10, 2010 7:52 AM
> To: [email protected]
> Subject: Existing standpipe in hig rise building
> 
> Scenario:  An existing high rise building is being retrofit with sprinklers.  
> The existing building has 6" standpipes throughout.
> Question:  Which of the following sections of NFPA 14 takes precedence 
> (5.4.1.2 or 5.4.1.3)?  Or in other words, does 5.4.1.3 apply to high rise 
> buildings?
> 
> 
> 5.4.1.2      Class I standpipe systems in buildings classified as high-rise 
> buildings shall be automatic or semiautomatic.
> 5.4.1.2.1    In buildings classified as high-rise, all required standpipes 
> shall be automatic or semiautomatic, including partial height and horizontal 
> standpipes that serve only a portion or limited number of floors within the 
> building
> 
> OR
> 
> 5.4.1.3    Where an existing standpipe system having standpipes with a 
> minimum diameter of 4 in. (100 mm) is to be utilized to supply a new retrofit 
> sprinkler system, the water supply required by Section 
> 7.10<http://codesonline.nfpa.org/a/c.ref/2010_ID02001400917/sec> shall not be 
> required to be provided by automatic or semiautomatic means, provided that 
> the water supply is adequate to supply the hydraulic demand of the sprinkler 
> system in accordance with NFPA 
> 13<http://codesonline.nfpa.org/a/c.ref/NFC13/book>, Standard for the 
> Installation of Sprinkler Systems.
> 
> 
> I have my response, but just wanted to see a technical discussion.
> 
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Support Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to