Daniel,

Number one is that you will have to remove the insulation BELOW the
wet piping that feeds the upper units. If batts you could simply
re-install the same insulation over the pipes. You DO NOT want to
encapsulate any piping between layers of insulation. Insulation is
just that--insulation. It retards the heat transfer between the
areas/objects it separates. If you sandwich the piping you not only
retard the heat loss from the pipe but you also retard the heat gain
from the room below. You must have heat input, which requires energy
and is therefore an active process, to sustain temperatures above
freezing when the ambient environment is below freezing. Insulation is
a passive system that slows heat loss or gain depending on which side
of the barrier your standing. Completely encapsulating will retard
both with loss winning in the end unless your original mass is
sufficient to retain the heat for the entire time you are experiencing
freezing temperatures. Note that the water in the ice cube tray
doesn't immediately turn to ice as soon as you put it in your freezer
but will in a flash freezer. The object is to make the piping be part
of the heated space (the R value of ceiling materials commonly used in
apartments is too little to be of consequence) so that the heat gain
from the room is greater than the heat loss to the attic.
Number two is blown in insulation will likely fail some day no matter
how you install it unless you build  dams along the runs of piping so
the insulation doesn't slide off your "tenting." The insulation is
fluid and will, like water, seek it's own level so that the R-38 you
applied throughout (which was probably more like R-32 over the piping
because it sits higher than the top face of the ceiling material that
the insulator will measure from, or maybe be full coverage since he'll
hump it over the pipe but then it will settle out over time) will
eventually fall to a lesser R value. And it you don't tent in some way
the insulation will flow under the pipes thus creating problem one.
"Developing a new antifreeze" would entail coming up with an additive
that lowers the freezing point of water and is, cheap, environmentally
friendly, not a health hazard, will stay in solution with the water
without the need for constant stirring, is simple to transport and
handle, and, of course, non-combustible. And there needs to be an
incentive that makes it worthwhile. Consider that glycerin and
propylene glycol have far greater use in the cosmetics, food, and
automotive industries, as those chemicals now exist, than they will
ever have in fire sprinklers. other chemicals in great abundance with
anti-freeze properties that we don't use in our industry are ethylene
glycol (highly poisonous) and alcohol (highly flammable). I'm no
chemist but I'm sure that there are other things equally dangerous for
our purposes out there already that lower the freezing point of water.
There are other chemicals that put out fires but they are impractical
for full buildings.
There are design solutions for the problem in the not yet built
buildings but the existing inventory will be a challenge. I'm
confident (but can't be sure with my crystal ball in the shop and all)
that the TIAs issued the other day will be modified and that some sort
of pre-mix will be allowed. For instance in Western Washington where
I've never seen temperatures below the high teens in the past 25 years
a solution below the combustibility threshold will probably work
whereas in Utah that probably wouldn't. In areas of Siberia the
utility pipes are above ground and in steam jackets because that's the
more effective way to lay pipe than burial.

On Fri, Aug 20, 2010 at 9:20 AM, Daniel Adams <[email protected]> wrote:
> Are there any thoughts or ideas concerning development of a new antifreeze
> which doesn't have the flammability issues of propylene glycol or glycerine
> (and the possible timeframe of when it could be on the market) ? A local
> fire authority I spoke with yesterday gave options of heat-tracing (or heat
> taping), insulation or a dry system to protect an apartment building which
> has a row of attic heads at the ridge and a layer of piping running on top
> of the bottom chords of the roof trusses to supply the heads in the units
> below. (The lower layer of pipe will be covered with R-38 loose fill
> insulation). How can it be determined if the R-38 insulation will adequately
> protect the piping below if it is revised into a wet-pipe system ? The
> piping that is above the insulation will likely be revised into a dry
> system. But this is only one job and thinking of all contractors and
> projects out there, the scope of these TIA's is pretty significant. I would
> imagine that somebody is working towards development of a new antifreeze
> formulation and just wanted to check if anyone has heard of such.
>
> Thanks,
> Daniel N. Adams
> Designer
> Interwest Fire Protection, Inc.
> 404 Ironwood Drive
> Salt Lake City, UT 84115
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA

253.680.7346

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to