Assuming the opening isn't complicated at the doors below, sounds like a MRA
of the rectangle high area in its entirety, and a 1500 MRA at lower ceiling.
One sets your pressure requirement (delta Elev)
One sets your highest flow (density over larger MRA).
Might want to consider bumping the riser to high part to balance a
bit.........

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, August 24, 2010 1:28 PM
To: [email protected]
Subject: RE: Remote Area

Matt-
Not unless the doors are open on the lower level.... 


Regards,
Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Tuesday, August 24, 2010 1:21 PM
To: [email protected]
Subject: RE: Remote Area

Can heat flow from one into the other?

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected]
> >[mailto:sprinklerforum- [email protected]] On Behalf Of Brian 
> >Harris
> >Sent: Tuesday, August 24, 2010 12:17 PM
> >To: [email protected]
> >Subject: Remote Area
> >
> >Quick question: Working on a project that is basically a rectangle 
> >with a large cylinder protruding up through the center of the 
> >building. The remote area will be the heads at the top of this 
> >cylinder but only totals 1000 sq.ft., do I need to pick up another 
> >500sq.ft. from part of the lower area?
> >
> >
> >Brian Harris
> >
> >
> >
> >
> >
> >
> >Design Engineer
> >
> >
> >
> >First Defense Fire Protection
> >11957 Ramah Church Road
> >Huntersville NC 28078
> >
> >
> >
> >
> >[email protected]
> >www.firstdefensefire.com <outbind://80/www.firstdefensefire.com>
> >
> >
> >
> >Ph: 704.948.3506
> >Fax: 704.948.3507
> >
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field) No virus found in 
> >this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.851 / Virus Database: 271.1.1/3089 - Release Date: 
> >08/24/10 01:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.18, Virus/Spyware Database: 6.15320)
http://www.pctools.com/ =======

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to