I haven't seen the flyer but I believe its in the neighborhood of 15 PSI.
The concern is the same as in steel pipe systems- huge amount of potential
energy with the possibility of rupturing piping in the case of CPVC. The
inevitable air pockets in a CPVC system undergoing acceptance testing at 200
PSI certainly has the air in the pocket at 200 PSI; but with the vast
majority of the piping filled with virtually incompressible water, the
amount of stored energy isn't as great. Most of us have heard the incredible
power of caps blowing thru block walls when there is a buildup of excessive
pressure in steel pipe systems.

The residential dry system will be tripped on sustained decay of air
pressure, based on the Potter QRS switch used in their electronic
accelerator. It might just open a solenoid since there is no need for a
differential-type DPV. Naturally residential systems will need to be
calculated for water delivery time, 15 seconds.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Tuesday, September 14, 2010 11:01 AM
To: [email protected]
Subject: Residential Dry Systems

  Has anyone seen the flyer for the new Tyco Residential Dry Pipe systems?
It states that it is listed for use with Tyco CPVC pipe and fittings.  I was
surprised to see the use of CPVC with a dry system.  I had always thought
that compressed air and CPVC was a very bad thing.

--
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to