They will definitely need a BFP on the domestic tap. They could end up needing a BFP on the fire line (probably should have one after the domestic tap so that standing water from the sprinkler system is not drawn into the domestic line). They should probably have a meter installed too. I doubt that the water company will be happy about giving them free domestic water through the fire line. The domestic demand will need to be added to the sprinkler demand when the total water through the main line is calculated.
Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, September 24, 2010 10:07 AM To: [email protected] Subject: Re: tapping fire lead in for domestic We are remodeling an an old grocery store, being converted into a church. The existing fire sprinkler is pipe schedule, 3 in lead in. Wet system, alarm check valve with an anti freeze loop. Off of city supply. Existing domestic supply is well water. The owner intends to tap the fire main lead in to run 1" domestic. My concern is that he is creating a cross connection with the fire sprinkler water and anti freeze loop. My secondary concern is tapping the fire sprinkler riser....should i recommend hydraulic calcs since they are modifying the supply of this existing pipe schedule system? I intend to notify the owner of my concerns in writing and recommend he consult with his Architect and Plumbing Engineer. Any recommendations? Forrest Wilson Cherokee Fire Sent from my Verizon Wireless Phone ----- Reply message ----- From: "Ron Greenman" <[email protected]> Date: Fri, Sep 24, 2010 10:26 am Subject: Pool as a water source To: <[email protected]> You can also use the pool for a heat sink for heat pumps and use a solar array to heat the pool to 50 degrees in winter (no freezing and the optimum heat transfer temperature for heat pump efficiency. Engineering kids. We're part of a group building a building. We don't drive the project nor is our part of the project an entity in a vacuum. On Fri, Sep 24, 2010 at 6:16 AM, Jamie.seidl <[email protected]> wrote: > I've done it here in Charlotte. No problems out of it yet, but it was just > the secondary source. We had an issue recently on a project that was a few > years old where we had to prove the velocity at the roof top pool with a > supply calc for the lowest system. The health department accepted it and > they re-opened the pool the next week. I would stress 2 inlets. The pool > contractor said that the largest inlet had a gpm velocity limit of 1400 gpm? > Maybe that was for both? > As far as a vortex plate, when we tested the pool, a vortex didn't develop > until we had less than 1' of water left, approx 40,000 gallons already > pumped, while my demand was around 32,000 gallons. I still sleep well at > night. > > Jamie > Sent from my iPhone > > On Sep 24, 2010, at 8:12 AM, "Dewayne Martinez" <[email protected]> wrote: > >> We have a owner that is requesting us to explore the possibility that a >> indoor pool be used as a water source for the sprinkler system. >> Anybody do this before? Seems like there would be too many problems >> with the chlorine in the water damaging the system components. >> Thanks, >> Dewayne Martinez >> Design Build Fire Protection >> New Berlin, WI >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email to:[email protected] >> (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)