Sammys in thick enough steel are listed for quite a bit of weight without
the retainer nut

-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Tuesday, October 12, 2010 1:00 PM
To: Thom; [email protected]
Subject: Re: A matter of conscience

The sprinkler piping may fall on the children because the hanger point of
attachment is insufficient. 

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Thom" <[email protected]>
Date: Tue, Oct 12, 2010 1:46 pm
Subject: A matter of conscience
To: <[email protected]>

As Ken said, it has been shown as an acceptable hanger along side of other
"Non-listable" hangers (Formed rods, U-hook and Wrap-around U-hook rods)
which have a long history of supporting fire sprinkler systems without
failure. I would be more concerned if you were in a seismic area, since
those loads are not from gravity primarily, as they are in FL.

The split ring hanger first appears in the 1999 Handbook Fig. A 6-1.1, prior
editions have a similar hanger called the "Malleable swivel Hanger"  I can't
tell you how many systems I've seen with split ring hangers, but it would
literally be hundreds if not thousands. Hanger failure for split rings must
not be a widespread problem of NFPA, the committee on hangers and bracing or
the CPS people would be all over it. 

Sleep well, those kiddies are not going to be knocked out because the split
rings are un-listed, but more likely because outside in FL they corrode to
the point of hanger failure, before they are replaced. 

Thom

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
ParsleyConsulting
Sent: Tuesday, October 12, 2010 8:47 AM
To: [email protected]
Subject: Re: A matter of conscience

  Thomas,

Figure A.9.1.1 in the '10 edition of -13 clearly shows a "split ring" 
hanger as a type of an "acceptable hanger", so my first thought is that 
if the rings themselves were listed, as they were required to be, you 
met the criteria established by the standard.

A quick look at two manufacturers catalog data showed neither had a 
listed split ring.

Just my thoughts.
-- 
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website


IMPORTANT NOTICE: This correspondence is not a Formal Interpretation 
issued pursuant to NFPA Regulations. Any opinion expressed is the 
personal opinion of the author and does not necessarily represent the 
official position of the NFPA or its Technical Committees. In addition, 
this correspondence is neither intended, nor should it be relied upon, 
to provide professional consultation or services.


  10/12/2010 6:30 AM, Thomas Watt wrote:
>    I was driving down the highway the other day when I passed a job I did
> about 4 or 5 years ago, a dry system (4"main w/2" branch lines) over a
> covered play area outside an elementary school. I had some reservations at
> the time but was told to follow the plan with the materials provided. What
I
> was concerned with at the time was installing Sammy screws vertically into
> boxed steel beams with no way to reach a back nut to install it. I had to
> drill pilot holes and oil the threads to help keep the Sammys from
breaking
> off.
>     The other problem I did not realize at the time but have become aware
of
> through my parasitic leaching from this remakably informative discussion
> group. Other than the 4" rings on the main, all of the hangers are the
> split-ring type. I remember reading here that they do not meet the
> requirements of NFPA 13 for hanging pipe.
>     Call me paranoid but I think that this system could fall given the
right
> set of circumstances. Remember, this system hangs above small children at
> play. Am I  obligated to inform the AHJ or some other entity?
>
> Thomas Watt
> A parasite/fitter/foreman (laid-off again)
> Orlando, Florida
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to