I believe this "there are louvers at the base of the skylight that are
closed when the room is to be blacked for use."  Thus there are there are
louvers at the base of the skylight that are OPEN (when the room NOT used?).
End of story.  Just like folding partitions in a conference room.  Sometimes
they are open sometimes they are closed, design for both.  It the louvers
were permanent and closed perhaps then maybe they could omit as a concealed
space.

Chris Cahill 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
ParsleyConsulting
Sent: Friday, October 22, 2010 1:11 PM
To: SprinklerFORUM
Subject: Skylights in remote area

Looking at a set of plans from a fire protection consultant today, 
responding to an earlier comment of mine which was:

"The sprinklers protecting the skylight area should be flowing in the 
hydraulic calculations for area X, as there is no physical separation 
which would allow them to be omitted".

The skylights are approximately 144 square feet in area, and 
approximately 4'-0" deep, protected by a single intermediate temperature 
upright sprinkler.

The response from the designer:

"The skylights in room XXX are like a small room or small compartment 
with a single fire sprinkler for protection; and there are louvers at 
the base of the skylight that are closed when the room is to be blacked 
for use. Therefore, per NFPA 13, 2007 ed. Section 22.4.4.6.2 these 
skylight sprinklers are allowed to be omitted from the hydraulic 
calculation. All ceiling sprinklers are designed and hydraulically 
calculated to cover the floor area, including the area below the 
skylight. The fire sprinkler in the skylights are only protecting the 
skylight cavity."

I disagree with their designation of this area as similar to a closet or 
bathroom meeting the intent of 22.4.4.6.2.

I'd welcome any thoughts on this perspective.
-- 

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to