And I think he should be fine as long as he is not more than 6" below the
bottom of the purlins, but then, I am a CEILING JET FREAK. Early this year
Roland straightened out a concerned poster by mentioning the MOMENTUM of the
ceiling jet- I thought 'ya, what Roland said', then I fire modeled some
set-ups, and thought 'YA, WHAT ROLAND SAID'!
 

-----Original Message-----
From: Ralphy Henderson [mailto:[email protected]] 
Sent: Tuesday, October 26, 2010 12:43 PM
To: [email protected]
Subject: RE: Maximum Deflector Distance below Z Purlins

I agree... that would mean the 12" from deck would come into effect. I think
9.2.4.2 (in the 07 ed) helps clarify what is meant by "bay" also.
As far as Mike's original post goes, with 9 1/2" z-purlins, he should be
fine as long as he's not more than 2 1/2" below the bottom of the purlins.

--- On Tue, 10/26/10, Matthew J. Willis <[email protected]> wrote:

From: Matthew J. Willis <[email protected]>
Subject: RE: Maximum Deflector Distance below Z Purlins
To: [email protected]
Date: Tuesday, October 26, 2010, 5:20 PM

Good question. It is not defined in Chapter 3; however, there are several
examples of "bay" throughout the standard. In particular note the figures
showing typical calc areas. "Bay" as I understand it, is the area between
the Frames that the purlin rest on.


R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Brad Casterline
> >Sent: Tuesday, October 26, 2010 11:54 AM
> >To: [email protected]
> >Subject: RE: Maximum Deflector Distance below Z Purlins
> >
> >It is something to think about I guess. But since the purlins are the
> >structural members impeding the heat flow, where does BAY come in?
> >
> >-----Original Message-----
> >From: Matthew J. Willis [mailto:[email protected]]
> >Sent: Tuesday, October 26, 2010 8:58 AM
> >To: [email protected]
> >Subject: RE: Maximum Deflector Distance below Z Purlins
> >
> >I always thought subsection (3) superseded when spaced in the bays.?
> >
> > R/
> >Matt
> >
> >
> >
> >Matthew J. Willis, CET
> >Automatic Fire Sprinklers
> >Norred Fire Systems L.L.C.
> >318-387-1134 Voice
> >318-816-1087 Mobile
> >318-387-1163 Facsimile
> >[email protected]
> >
> >> >-----Original Message-----
> >> >From: [email protected] [mailto:sprinklerforum-
> >> >[email protected]] On Behalf Of Brad Casterline
> >> >Sent: Monday, October 25, 2010 2:00 PM
> >> >To: [email protected]
> >> >Subject: RE: Maximum Deflector Distance below Z Purlins
> >> >
> >> >If the purlin spacing does not exceed 7'-6", I think so.
> >> >
> >> >-----Original Message-----
> >> >From: Bobby Gillett [mailto:[email protected]]
> >> >Sent: Monday, October 25, 2010 1:53 PM
> >> >To: [email protected]
> >> >Subject: RE: Maximum Deflector Distance below Z Purlins
> >> >
> >> >If my understanding is correct, this is considered obstructed
> >> >construction
> >> >now so it would be per 8.6.4.1.2 and if the scenario is typical to
> >most
> >> >purlin buildings you should be able to utilize 8.6.4.1.2 (1) 1"-6".
> >What
> >> >say
> >> >everyone else?
> >> >
> >> >
> >> >
> >> >Bobby Gillett
> >> >
> >> >Sr. Project Manager
> >> >
> >> >Key Fire Protection, Inc.
> >> >
> >> >(731) 424-0130 office  (731) 424-9285 fax
> >> >
> >> >(731) 267-4853 cell
> >> >
> >> > <mailto:[email protected]>
> >> >[email protected]
> >> >
> >> >
> >> >
> >> >
> >> >
> >> >  _____
> >> >
> >> >From: [email protected]
> >> >[mailto:[email protected]] On Behalf Of Mike
> >> >Hairfield
> >> >Sent: Monday, October 25, 2010 1:44 PM
> >> >To: AFSA SprinklerFORUM
> >> >Subject: Maximum Deflector Distance below Z Purlins
> >> >
> >> >
> >> >
> >> >
> >> >
> >> >OK Metal building with 9 1/2" Z-Purlins, what is maximum distance that
> >> >the
> >> >deflector can be below the
> >> >bottom of the Purlin.
> >> >
> >> >Mike
> >> >_______________________________________________
> >> >Sprinklerforum mailing list
> >> >[email protected]
> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> >For Technical Assistance, send an email to: [email protected]
> >> >
> >> >To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> >(Put the word unsubscribe in the subject field)
> >> >
> >> >  _____
> >> >
> >> >No virus found in this message.
> >> >Checked by AVG - www.avg.com
> >> >Version: 10.0.1152 / Virus Database: 422/3218 - Release Date: 10/25/10
> >> >
> >> >_______________________________________________
> >> >Sprinklerforum mailing list
> >> >[email protected]
> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> >For Technical Assistance, send an email to: [email protected]
> >> >
> >> >To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> >(Put the word unsubscribe in the subject field)
> >> >
> >> >_______________________________________________
> >> >Sprinklerforum mailing list
> >> >[email protected]
> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> >For Technical Assistance, send an email to: [email protected]
> >> >
> >> >To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> >(Put the word unsubscribe in the subject field)
> >> >No virus found in this incoming message.
> >> >Checked by AVG - www.avg.com
> >> >Version: 9.0.862 / Virus Database: 271.1.1/3204 - Release Date:
> >10/25/10
> >> >01:34:00
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.864 / Virus Database: 271.1.1/3204 - Release Date: 10/26/10
> >01:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to