Sorry for the delay Brian - yes, 8.17.5.1.3 is referring to small hose connections only. But Cliff's comment isn't entirely accurate in that the building code allows for certain conditions where 2 1/2" fire hose valves can be directly connected to a sprinkler system and are not considered to be a standpipe system, nor required to be a separate system in that regard.
Steve -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris Sent: Wednesday, October 27, 2010 1:18 PM To: sprinklerforum@firesprinkler.org Subject: RE: 1-1/2" & 2-1/2" Hose Connections Cliff- Thanks, will do. Brian Harris FDFP Inc. -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff Whitfield Sent: Wednesday, October 27, 2010 4:06 PM To: sprinklerforum@firesprinkler.org Subject: RE: 1-1/2" & 2-1/2" Hose Connections Brian, I believe that 2½" hose valves are pretty much governed by NFPA 14. You might look there for some guidance. Cliff -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris Sent: Wednesday, October 27, 2010 3:01 PM To: sprinklerforum@firesprinkler.org Subject: FW: 1-1/2" & 2-1/2" Hose Connections Anybody? Brian Harris FDFP Inc. _____ From: Brian Harris [mailto:br...@firstdefensefire.com] Sent: Tuesday, October 19, 2010 3:38 PM To: 'sprinklerforum@firesprinkler.org' Subject: 1-1/2" & 2-1/2" Hose Connections Can someone confirm for me that the hose connections talked about in 8.17.5.1.3 are the Small (1-1/2") type only? If so what are acceptable supply points for 2-1/2" hose connections? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16170) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16170) http://www.pctools.com/ ======= ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16170) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)