I'm designing a residential project using res. heads (LFII) and designing to 
full NFPA 13.  When I calc my four heads using the "design area", I am 
wondering 
if I can use the room design method to determine my sprinkler demand?  For 
instance, I have a room that measures 16' X 16', (256 sq. ft.) but the head is 
actually located 10 feet off of the 2 adjacent far walls.  If using the flow 
rates from the chart I know that I need to flow 20 gpm from that head based on 
my maximum 20' x 20' spacing.  But If I'm using the .10 over the "design area" 
can I just use the demand of 25.6 gpm for that head (16' x 16' sq. ft.) versus 
the 40 gpm based on 20' x 20'?  I understand then I would then base my system 
requirements on the more demanding of the two methods.  I can flow all four 
heads at a 20 gpm no problem, but the 40 gpm from just one head.....ouch!
I haven't done residential in a looooong time, so thought I'd check for the 
heck 
of it and I'm pretty sure I'll find instead that I'm full of it!   
Thanks in advance!
 
Carrol Glimstad


      