The steel  pipe and fittings we use are rated (not listed 'cause they
don't need to be) at 150 psi WOG. WOG is water, oil, gas. The 150 is
for gas and the fluid rating is twice that (300 psi) which is why we
can use the same old pipe in those systems where we need 250 psi
listed sprinkler components.

On Thu, Nov 11, 2010 at 2:29 PM, Thom <[email protected]> wrote:
> I personally would not worry about the heads, not being rated for the 215#
> As stated below the 200 Psi is the minimum test pressure or as 13 says "or
> 50# over operating pressure" so test it to 265# for 2hours and sleep well.
> 175# is operating pressure and your operating pressure is 50Psi air most of
> the time. True if the system trips your operating pressure is then 215#, but
> it will not be a sustained pressure, as they will drain and reset the
> system, and no way will it exceed the test pressure of 265.
>
>
>
>
>
>
>
> Even still 215 is not that big of a deal since you'd be testing at 200 psi
> minimumCraig Prahl
> CH2MHILL/SPB
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to