If someone is serious about eliminating the required fire sprinklers, let
them hire an FPE with fire modeling capabilities to prove that they would
not be effective and provide the "Equal" protection required by codes and
standards. Their money, their time if it doesn't work out or the AHJ rejects
the plan.

Subject: RE: Omitting sprinklers in a high building

If the building code considers this an F-2 occupancy and the building can
meet the egress requirements without sprinklers, and there are no other code
issues that would require sprinklers then they would be correct that you
wouldn't need sprinklers.  It has nothing to do with building height.

Even if the building were 100 feet hight, if a fire were to break out the
products of combustion are going where, to the heighest point.  Sprinklers
may react slower due to the height but at some point they are going to react
and will help knock down the gas temps.   I've asked the same question and
had gotten this answer back from different mfgr engineers.  They are the
ones doing the design, testing and listings for the sprinklers and I hope
they would know.

So to say that just because the building is high there shouldn't be any
sprinklers is not valid.  If the biulding were an F-1 occupancy you'd have
sprinklers period.  Otherwise you don't meet code.

To sprinkler or not to sprinkler is not up to NFPA 13, it's a building code
issue.
 
Craig Prahl
CH2MHILL/SPB
864-599-4102

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to