In a 4 story apartment building with 2 levels of parking below, the AHJ has specified a design density of .20 gpm /sq. ft. to be used throughout. The construction is of composite joists (TJI's) which are not completely filled with insulation.
If designed using residential heads, under Special Design Approaches, section 11.3.1 (in 2007 NFPA 13) the area would be 4 heads [and the .20 density would be used in lieu of .10 as specified in 11.3.1.2 (2)] Daniel N. Adams Designer Interwest Fire Protection, Inc. 404 Ironwood Drive Salt Lake City, UT 84115 Phone: (801) 746-4040 Fax: (801) 746-4043 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)