Your question only asked about Class, but other factors are important.

I think this would be designed for Group A plastics because you haven't
provided enough information to provide other advice.  Seems you have Class
IV and maybe encapsulated but you haven't mentioned this possibility.  Of
course the mixed commodity approach could also be used to reduce the design
classification, but severe restrictions would be placed on stored quantities
and locations of the more hazardous materials.  Under the 2007 edition the
roof height plays a role in determining densities if Roof Height - Storage
Height > 20 ft.  Are you thinking about two approaches - one approach for
the 20 ft storage and one approach for the 6 ft storage?  What about other
commodities such as flammable/combustible liquids?  Is there an Owner's
Information Certificate?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Adams
Sent: Wednesday, December 01, 2010 8:54 PM
To: [email protected]
Subject: Re: White Cap Contractors Supply


I have a question for the forum.  We have a contract to retrofit an existing
building for a "White Cap Construction Supply".  This company sells a wide
variety of items and no one item has a high concentration.  Rack storage is
a maximum of 20'.  Racks cover roughly 60 to 70 percent of the area and the
balance is cantilever racks 6' high.  This has mixed Commodity Class with in
our opinion is class II, III, & IV, and possibly small areas of group "A"
plastics.  What class should this be designed to ?  If you are not familiar
with this company you can see there web site at www.whitecap.com.  Any
advise would be appreciated.

Sincerely,


Jim Adams
Total Fire Systems





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to