Jack,
This is only regarding combustible concealed spaces.  It sounds like your 
situation is not, so you won't need to apply 20 psi.

Bob Knight

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jack Linus
Sent: Monday, December 06, 2010 1:13 PM
To: [email protected]
Subject: Sloped smooth ceiling and minimum pressure

Hello Is 8.6.2.2.1.1 relevant only for the last construction type in table 
8.6.2.2.1 (a)?
I have a sloped smooth ceiling with pitch 5/12. Do I have to use 20 psi, if the 
spacing perpendicular to the slope exceeds 8 ft ? The area below the sloped 
ceiling is a restaurant seating area. Best regardsJack Linus


      