Joe,

It was removed prior to the 2007 edition, that's what the little dot means between 8.6.4.1.4.3 and the renumbered 8.6.4.1.4.4.

Comment 13-145 (Log #269) in the 2006 ROC showed the reasons to delete it, and allow the text of 8.3.4.3 to cover the issue. Our friend Cecil was the submitter on that comment. The substantiation read as follows: The new verbiage for 8.3.4.3 allows K-4.2 sprinklers and would therefore allow the 4.2 k factor sprinkler in attics when the 20 psi minimum would not necessarily be required.

Vote in favor of this comment was 29-0 in favor of accepting.

Further information on 4.2k sprinklers and galvanized pipe is also in Comment 13-157 (Lot #240) in that same document. The substantiation for that read as follows: The only reason for section 8.6.4.1.4.4 in the 2002 edition was to allow k-4.2 sprinklers in dry-pipe systems in this one situation, since section 8.3.4 did not generally allow such sprinklers. Now that section 8.3.4 has been modified by proposal 13-202, there is no need for this section to appear in the attic rules. The section also causes problems for wet pipe systems using k-4.2 sprinklers. AHJ’s have argued that in order to use k-4.2 sprinklers on a wet pipe system, the pressure needs to be 20 psi. This was never the intent of section 8.6.4.1.4.4 but the words can be read that way. The problems are all resolved if the section is eliminated and the rules for k-4.2 sprinklers are all in section 8.3.4 where they belong.

Vote on this comment was 29-0 in favor of accepting in principal, and referred back to 13-145.

That's the best info I could find.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 12/7/2010 11:19 AM, Joe Burtell wrote:
Where did this section go from the 2002 in the 2007 or 2010?
8.6.4.1.4.4 Nominal K-4.2 orifice sprinklers shall be permitted for use at
the 20 psi minimum pressure option for wet pipe systems and dry pipe systems
where piping is corrosion resistant or internally galvanized.

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [email protected]
Web Site: http://www.burtellfire.com



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
  • 4.2 K Joe Burtell
    • RE: 4.2 K Brad Casterline
    • Re: 4.2 K ParsleyConsulting

Reply via email to