Very true. But I find if you understand where they screwed up, it helps out when you do.


At 06:11 PM 12/16/2010, you wrote:
I'd keep the work YOU do to a minimum and simply respond with an email asking how .58x2000>1160 and let them find it.
It's THEIR screwup, you're paid to review, not do the design.

George Church'
Rowe Sprinkler
[email protected]
570-837-7647

-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Thursday, December 16, 2010 5:43 PM
To: [email protected]
Subject: RE: 0.58 over 2000

Not crazy, just someone who knows what he's looking at.  Kudos!

As others have stated, there's a whole number of reasons this could happen.
You can either reject the submittals outright (and make the designer figure out where he/she went wrong), or spend the time to figure it out yourself.
Either way, it's nice to see a plan reviewer pick-up on something like that.


Ed Kramer
Littleton, CO



> Reviewing a hydraulic calc for a 0.58 over 2000 gridded warehouse
> system.
> All seemed OK until I reached the BOR flow of 1143 gpm.  From this I
> assume the selected design area isn't correct since there's no way a
> 0.58 over
> 2000
> system should flow less than 1160 gpm.  I've never heard of hydraulic
> imbalance that results in lower overall flow.  Am I crazy or is there
> a new version of sprinkler hydraulics out there?
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to