As I recall from my days as an inspector we were not required to look t every little detail. There were certain areas or items that required detailed inspection and after that ewe were to use reasonable judgement regarding the depth of the rest of the inspection. A contractor with workers that had a good reputation with the inspector got a more cursory inspection than a stranger or known quick buck artist.
On Sun, Jan 23, 2011 at 7:19 PM, Jim Davidson <[email protected]> wrote: > John, > > If I remember correctly, a "miss" by a code official does not mean the system > is acceptable. The permit the contractor takes out at the beginning of the > job requires that the system is installed by the referenced code that is > adopted by the jurisdiction where the project is located and a variance to > the code is required to be written on the AHJ's letterhead, if not the > contractor is required to install by code. > > John you are correct in that "only time will tell if a violation results in > an incident." Along with meeting someone's lawyer(s) > > Jim Davidson > > Davidson Associates > Fire Protection * Medical Gas * Code Consulting > 302-994-9500 Fax:302-234-1781 > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of John Drucker > Sent: Sunday, January 23, 2011 8:31 AM > To: [email protected] > Subject: RE: Rolling medical file storage > > Violations have no concept of time. However only time will tell if a > violation results in an incident. > > John Drucker, CET > Fire Protection Subcode Official > Fire/Building/Electrical Inspector > Fire Marshals Office > Borough of Red Bank, NJ > > Not the official position of any agency, association, committee or > otherwise. Obtain required applications, permits, inspections and approvals > from Authority(s) Having Jurisdiction. > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of George Church > Sent: Saturday, January 22, 2011 2:26 PM > To: [email protected] > Subject: RE: Rolling medical file storage > > A competitor claimed a finishing nail was an acceptable hanger because the > system had been inspected and accepted by the local BCO- who I hope didn't > walk the attic with his eyes closed and missed it. > > So, its ok until time eternal (or a major renovation) if an inspector missed > an obvious code violation during the acceptance inspection & testing? > > Like the system showing a static less than the demand at flow? > glc > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Thursday, January 20, 2011 2:46 PM > To: [email protected] > Subject: RE: Rolling medical file storage > > Movable racks are supposed to be protected the same as multi-row racks. So > based on the design there could be a violation. But every questionable > system has always "been installed that way and accepted" by someone no one > can remember. > > > > Craig L. Prahl, CET > Fire Protection > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Matthew J. > Willis > Sent: Thursday, January 20, 2011 2:33 PM > To: [email protected] > Subject: RE: Rolling medical file storage > > I am surprised it is not a deluge.... > > If they were put in since last inspection, Yes code violation. (4.1.6) > > If built that way, No. (1.1.2) > > > > R/ > Matt > > > > > > Matthew J. Willis, CET > Automatic Fire Sprinklers > Norred Fire Systems L.L.C. > 318-387-1134 Voice > 318-816-1087 Mobile > 318-387-1163 Facsimile > [email protected] > >> >-----Original Message----- >> >From: [email protected] [mailto:sprinklerforum- >> >[email protected]] On Behalf Of Gregg Key >> >Sent: Thursday, January 20, 2011 1:27 PM >> >To: [email protected] >> >Subject: Rolling medical file storage >> > >> >It has been a while since I have been on and I think this has been >> >discussed >> >before but cant find it in the archives so here I go. >> > >> >Doing a NFPA 25 inspection and find a medical storage room with rolling >> >files that are within 8" of the sprinklers. Sprinklers spaced 12x12. This >> >system has 8 rolling files and only room for 1 to be open at a time so no >> >way to get adequate coverage. Was told it was installed like this from >> >beginning and was accepted. What sayest the Sprinkler forumites? code >> >violation or not? How would you address it? BTW this is at a State >> >facility. >> >Thanks >> > >> >C.Gregg Key, SET >> >Key Fire Protection Services,Inc >> >Project Manager >> >(O) 706-790-3473 >> >(C) 706-220-8821 >> > >> >_______________________________________________ >> >Sprinklerforum mailing list >> >[email protected] >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> > >> >For Technical Assistance, send an email to: [email protected] >> > >> >To Unsubscribe, send an email to:[email protected] >> >(Put the word unsubscribe in the subject field) >> > >> >No virus found in this incoming message. >> >Checked by AVG - www.avg.com >> >Version: 9.0.872 / Virus Database: 271.1.1/3375 - Release Date: 01/19/11 >> >13:34:00 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)