these are CRAZY restrictions

On Tue, Feb 15, 2011 at 5:01 PM, Thom <[email protected]> wrote:

> If you can't meet the restrictions for Specific application sprinklers, you
> would revert to Standard spray sprinkler or other listed sprinkler for use
> in concealed combustible spaces or attics. All the exclusions and
> exceptions
> in NFPA 13 would apply.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> Sent: Tuesday, February 15, 2011 3:08 PM
> To: [email protected]
> Subject: COIN sprinklers
>
> OK, I have yet to find a space that fits the listing restrictions on wither
> make of these special sprinklers for flat concealed spaces...
>
> AND tech support doesn't seem to have the answers either.. We have one more
> similar space - 1 on 12 pitch, 2 x 12 joists at the roof BUT there are
> girder trusses about 18" wide spaced approx. 16'-0 on center that create
> spaces 18" wide x 56' long that are well over 36" deep. The peak is also
> 37"
> clear between the bottom of joists to the top of the ceiling.
>
> It doesn't fit in the box, and the Owner has no money to provide draft
> stops
> as required by the listing....
>
> What do we do??
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850 <+18509371850>
> fax 850-937-1852 <+18509371852>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to