The test interval is determined by 49 CFR and DOT regulations and the cylinder 
marking at the neck of the cylinder depending on the "stamped" cylinder marking 
the hydrostatic test can be extended by five years, testing should be as per 
Compressed Association Guidelines C-1 "Methods of Hydrostatic Testing of 
Compressed Gas". Unless specifically noted the testing guidelines in 49 CFR if 
more stringent than NFPA will supersede.

Have a fire safe day!

Jim   

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ford, Charles
Sent: Thursday, February 17, 2011 11:31 AM
To: [email protected]
Subject: RE: Inergen hydrotest

Actually, I now see your point. CFR 49 is more he "how" and 2001 is what I 
needed, the "when" 


C. Burton Ford
Nicet Certified
Special Hazards IV
Fire alarm IV
Sprinkler III
Water Based Inspections I
NFPA Certified Fire Protection Specialist [CFPS]
Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of [email protected] 
[[email protected]]
Sent: Thursday, February 17, 2011 11:11 AM
To: [email protected]
Subject: RE: Inergen hydrotest

NFPA 2001 (2008) references CFR 49 for the DOT requirements for cylinders.
No specifics are in NFPA 2001.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]



  From:       "Ford, Charles" <[email protected]>

  To:         "[email protected]" 
<[email protected]>

  Date:       02/17/2011 09:35 AM

  Subject:    RE: Inergen hydrotest

  Sent by:    [email protected]






Anybody know the hydrotest requirements for inergen cylinders and where it
is referenced?  NFPA 2001?

C. Burton Ford
Nicet Certified
Special Hazards IV
Fire alarm IV
Sprinkler III
Water Based Inspections I
NFPA Certified Fire Protection Specialist [CFPS]
Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401
________________________________________

This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not a
named addressee you are hereby notified that you are not authorized to
read, print, retain, copy or disseminate this communication without the
consent of the sender and that doing so is prohibited and may be unlawful.
Please reply to the message immediately by informing the sender that the
message was misdirected.  After replying, please delete and otherwise erase
it and any attachments from your computer system.  Your assistance in
correcting this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to