Good morning.
Thanks to all of you for your great answers.
I see this in my first training with AFSA in 2004 (great raining) but once
you are in the field, you have a lot of questions.
I see a lot of times some designers who use in all cases the maximum
coverage per sprinkler to do their hydraulic calculations, and when I ask
them about the "As", they tell me that us the maximum coverage (based on the
hazard classification) is a "Best Practice" because you do not need to find
what is the largest sprinkler coverage in the hole system. With this forum,
now I know I always need to use the maximum "As" in my most hydraulic
demanding area, and that value will be used for the calcs.
Regards and thanks to all of you.

Gerzayn Fuentes
CEPI.mx
Mexico
Tel +52 (81) 17660800


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to