Good morning. Thanks to all of you for your great answers. I see this in my first training with AFSA in 2004 (great raining) but once you are in the field, you have a lot of questions. I see a lot of times some designers who use in all cases the maximum coverage per sprinkler to do their hydraulic calculations, and when I ask them about the "As", they tell me that us the maximum coverage (based on the hazard classification) is a "Best Practice" because you do not need to find what is the largest sprinkler coverage in the hole system. With this forum, now I know I always need to use the maximum "As" in my most hydraulic demanding area, and that value will be used for the calcs. Regards and thanks to all of you.
Gerzayn Fuentes CEPI.mx Mexico Tel +52 (81) 17660800 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)