Commissioning per NFPA 3, but what's that?   I see it on a list with "Easter 
Bunny", "Tooth Fairy" and "Great Pumpkin".

SML

   
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Cliff Whitfield" <[email protected]>
Sender: [email protected]
Date: Thu, 3 Mar 2011 16:38:19 
To: <[email protected]>
Reply-To: [email protected]
Subject: RE: Cx

Craig,

My guess is 'Commissioning'.

Cliff Whitfield, SET
President
Fire Design, Inc.
3784 Holly Ridge Trail
Marianna, FL 32448
Ph: 850-526-1886
Fx: 850-526-1884
 
[email protected]
www.fire-design.com
 
 
 -----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, March 03, 2011 4:31 PM
To: [email protected]
Subject: RE: Cx

CX?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, March 03, 2011 5:18 PM
To: [email protected]
Subject: Cx

Understand still no LEED points  for sprinklers and we haven't released the
RP for Cx and Integrated Testing yet.....
So without points and without a procedure to follow, I think we're talking
infancy.

However, I live in the sticks- but I do get out occasionally ;) and
occasionally communicate with others in the business when we venture across
the county line :)
I'm not hearing anything approaching Cx being mainstream.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, March 03, 2011 3:50 PM
To: [email protected]
Subject: Re: As = L x S

WHEN? IF..

On Thu, Mar 3, 2011 at 12:35 PM, Thom <[email protected]> wrote:
> Just a follow up on "AS Built" drawings, won't they become "Common" 
> practice as NFPA 3 Commissioning becomes more common???
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George 
> Church
> Sent: Thursday, March 03, 2011 12:04 PM
> To: [email protected]
> Subject: RE: As = L x S
>
> Pain in ...
> Similar to badge heavy in this usage.
>
> George Church
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad 
> Casterline
> Sent: Thursday, March 03, 2011 1:44 PM
> To: [email protected]
> Subject: RE: As = L x S
>
> All true George, and maybe I worry a little too much, but when Gerzayn 
> mentioned "Best Practice", the idea of not all heads ending up exactly 
> as planned occurred to me. I left out the part about calcing all 
> sched. 40 and figuring total pressure at all flowing outlets, not just 
> a few! Have you ever had to "check your back pockets", because you 
> still needed a little more? :) What does PIA stand for, can you say in
public?
>
> -----Original Message-----
> From: George Church [mailto:[email protected]]
> Sent: Thursday, March 03, 2011 12:28 PM
> To: [email protected]
> Subject: RE: As = L x S
>
> In all seriousness, I find submission of AsBuilts in this industry as 
> the exception rather than the rule, and the likelihood of AsBuilt 
> Calcs even more remote, absent a contractual obligation and an 
> engineer either smart enough or PIA enough to followup.
>
>
>
>
> Not saying they aren't a great idea for those whose systems don't 
> closely resemble the original layout, just saying that it isn't 
> exactly a mainstream issue. Absent buildings burning to the ground 
> and/or people dying due to improper installation, we don't need to add 
> the cost and if you want to see a contractor avoid something, how 
> about taking the chance that their calc will indicate they need to go 
> back into t a recently completed project and make changes! Now the 
> building is occupied, now the drywall ceiling is up and tested- I can 
> tell you the GC isn't looking to enforce since it'll cause hardship for
all.
>
> George Church
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad 
> Casterline
> Sent: Thursday, March 03, 2011 9:17 AM
> To: [email protected]
> Subject: RE: As = L x S
>
> Something else you might want to keep in mind is the idea of "AS-BUILT 
> CALCULATIONS". Say you calc an Ord. Haz. II at 104 SF/head because the 
> heads are 6'-6" from one wall and 4'-0" from another. But there is a 
> conduit at 4'-0". The fitter knows 130 SF max for standard coverage 
> heads in Ord. Haz., so 5'-0" is fine. You might have a little trouble 
> with the as-built calcs in this case!
>
> *******************************************
> Good morning.
> Thanks to all of you for your great answers.
> I see this in my first training with AFSA in 2004 (great raining) but 
> once you are in the field, you have a lot of questions.
> I see a lot of times some designers who use in all cases the maximum 
> coverage per sprinkler to do their hydraulic calculations, and when I 
> ask them about the "As", they tell me that us the maximum coverage 
> (based on the hazard classification) is a "Best Practice" because you 
> do not need to find what is the largest sprinkler coverage in the hole 
> system. With this forum, now I know I always need to use the maximum 
> "As" in my most hydraulic demanding area, and that value will be used for
the calcs.
> Regards and thanks to all of you.
>
> Gerzayn Fuentes
> CEPI.mx
> Mexico
> Tel +52 (81) 17660800
>
>
>
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
  • Cx George Church

Reply via email to