Good morning.
I have a storage building that has:
- Carton boxes over the floor with a height of 11.5 ft.
- PET in bags, where each one weigh is 1 TON
- Wood Pallets over the floor with a height of 11.5 ft.

The building has 27ft height.

Looking in NFPA 13 ed.2007 I found the following design criteria:
- Wood pallets: Table 12.12.1.2(d) = 12 head K25.2 @ 15psi + 250gpm @
60min.
- Carton boxes: Table 14.4.1 = 12 head K25.2 @ 15psi + 250gpm @ 60min.
- PET: Table 15.2.5a = 0.60 @ 2,500 sq.ft. + 500gpm @ 150min.

All the materials are mixed in the floor, so I need to decide for just one
design criteria for the entire building.

The density for K25.2 @ 25psi is 0.98gpm/sq.ft. if the maximum "As" per
head is 100 sq.ft. This is more that 0.60 gpm/sq.ft.

I think that wood pallets and carton boxes needs more water to suppress.
And PET need less water to control, but more heads will open because
generate mote heat that carton or wood pallets.

What should be the design criteria for this storage building?
Best regards!

Gerzayn Fuentes
CEPI - Monterrey, Mexico.
Tel. +52 (81) 1766-0800
www.cepi.mx







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to