Section 8.4 shows the application requirements by type of sprinkler. That's where it says for residential and ESFR wet pipe only (unless listed for dry). Since 8.4.3 on EC does not have such a statement, there is no such restriction.

Roland

On Mar 24, 2011, at 6:10 AM, Matt Grise wrote:

Forum,

I am having a little brain glitch this morning: Can EC heads be used on dry pipe systems?

Thanks,