This is off topic, but I have just seen a sprinkler design that is out for
tender. One building having two separate water supplies and system risers.
Every room in this builsing are fed from both systems. So each system
supplies every alternate sprinkler line. Taken individually, each system
provides light hazard coverage, and together, they provide ordinary hazard
coverage. Just when I was thinking that I had seen them all.

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: April 8, 2011 9:01 AM
To: [email protected]; [email protected]
Subject: RE: Concealed Sprinklers Limited to Ordinary Hazard Spacing

In other words, a light hazard occupancy with two different areas of
coverage depending on the type of head?  Sounds like the engineer is
concerned about the response time of the concealed heads vs the recessed.
Maybe he/she attended a recent performance design seminar and doesn't
realize we are dealing with rules and not engineering design.  Are the
concealed installed at a higher elevation than the recessed?  NFPA 72
adjusts detector spacing for ceiling height, but so far NFPA 13 does not
build this in.   Are you in charge of selecting the sprinkler type?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike Hill
Sent: Friday, April 08, 2011 9:39 AM
To: [email protected]
Subject: Concealed Sprinklers Limited to Ordinary Hazard Spacing

This may have been covered in the past, but I did not see any mention of it.

 

Recently we have seen contract specifications requiring that concealed
sprinklers be spaced for ordinary hazard requirements, while allowing
recessed sprinklers to be spaced for light hazard requirements in the same
space. Does anyone know where this requirement may be coming from? Want to
make sure I didn't something.

 

Michael Hill

Vice President

 

Phoenix Fire Protection, Inc.

(301) 669-7066

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to