Still seems that if there fuel in the tanker the lower portion will have more 
mass and be better able to ameliorate against rapid heat absorbtion.

Ron Greenman 
...On the phone

On Apr 8, 2011, at 10:33 AM, Roland Huggins <[email protected]> wrote:

> I suspect some of the confusion stems from not defining the objective of the 
> spray system.  As Scot was discussing, it is typically there to address the 
> radiant heat from an adjacent fire.
> 
> Roland
> 
> 
> On Apr 8, 2011, at 7:46 AM, Chris Cahill wrote:
> 
>> Ok maybe there is some confusion on my part.  You and at least some one else 
>> suggested the lower area needs the most help.  Could you explain.  The area 
>> with fuel inside needs NO help from sprinklers.  It's only the dry steel on 
>> the inside that is an issue.  Certainly the bottom in a case of an empty 
>> tank needs help.  But no more that the top of a nearly full tank.
>> 
>> Not arguing you don't need sprinklers on the bottom, because you don't how 
>> much fuel is present when the fire starts.  I concur heads are need.  Just 
>> why the more important.
>> 
>> Chris
>> -----Original Message-----
>> From: å... .... <[email protected]>
>> Sender: [email protected]: Fri, 8 Apr 2011 
>> 03:40:30
>> To: <[email protected]>
>> Reply-To: [email protected]
>> Subject: Waterspray Systems for LPG tankers
>> 
>> sub-equatorial spray helps
>> where help is needed most.
>> on the wetted underbelly.
>> 
>> but to say direct impingement is necessary
>> when the proper flux is delivered from the sides and above
>> might do more to sell sprinklers
>> than belay our fears.
>> 
>> Most prescriptions were well intended
>> (for the sales reps and for fire protection),
>> but not all of the older prescriptions
>> were substantiated.
>> 
>> when Nature starts reading more NFPA,
>> is when I start believing what each
>> 30-year old prescription has to say.
>> (sure I do it anyway, but don't be fooled
>> just because its a written rule).
>> 
>> I am still sticking with
>> what I have been seeing:
>> run down happens.
>> 
>> scot deal
>> excelsior fire
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> For Technical Assistance, send an email to: [email protected]
>> 
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> For Technical Assistance, send an email to: [email protected]
>> 
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to