Craig,

We have done a couple industrial sites with this combination. No check valve no 
floor control valve. I guess I always read 14 to be talking about wet systems 
specifically. Steve and the others bring up a good point that it doesn't 
differentiate. Truth be known , anyone who works on industrial sites much also 
understands that time after time engineering and ingenuity have to come into 
play because the standard doesn't address so many of the situations that come 
up. 

Rod

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, April 22, 2011 7:49 AM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

Yes the riser is in a heated enclosure.  There is no advantage in running 
separate risers for standpipe and sprinklers.  For industrial structures like 
this the approach is common. Also space allocation is premium in these types of 
facilities.  

While it might be easier from a design standpoint, from an installation 
standpoint, not easy by a long shot.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Friday, April 22, 2011 9:23 AM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

Craig, are you trying to save the owner's money by attempting the combined
dry sprinkler and standpipe system, or has the owner dictated this approach?
I assume you are running your sprinkler system from a heated valve
enclosure.  Seems it would be easier to have separate systems starting from
that point.
 
Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, April 22, 2011 8:48 AM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

Check valve = worthless in a dry system as I have described.  Same goes for
the floor control valve.  If you are going to service one floor and close
that valve to isolate the section, you can't just reopen it once you're done
working or the air pressure loss in that part of the system will set off the
dry valve.  So unless you're going to crack the valve open really really
slow so the compressor can keep up with the pressure changes and you don't
mind spending the day playing with that, the floor control assemblies have
no purpose in the dry systems.  This may be exactly why they are
specifically mentioned for wet systems.

NFPA is really silent when it comes to special conditions in industrial
installations such as this.  These are special hazard operations that often
fall under the criteria of the owner's risk management or their underwriter.
Conventional thought processes often don't apply and won't work.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Friday, April 22, 2011 7:14 AM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows

NFPA 14 6.3.5 doesn't make any exception for dry combined systems, at least
that I can see, the annex material has diagrams that are clearly for wet
pipe systems, but the wording really doesn't leave any wiggle to get out of
doing it on non wet systems.  It applies any time a sprinkler system
connection is made to a standpipe, so regardless of whether or not the
building is considered multi story if you take off at each level from the
standpipe to a sprinkler system you are by code required to provide a
shutoff and check.  The check valve seems a bit silly in this case, but I
can understand why they'd want a control valve (similar to the requirements
for each vertical standpipe to have its own valve to allow maintenance
without taking the entire system out of service).
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com

________________________________

From: [email protected] on behalf of
[email protected]
Sent: Thu 4/21/2011 7:14 PM
To: [email protected]
Subject: RE: Combination standpipe riser & hose flows



But is that for wet systems?   For a dry system such as this the shut off
valves and check valves would serve no purpose.  The system is either
totally flooded due to head(s) fusing or it's dry.

For the application I have, there is no real building code correlation to an
occupied mult-story buildings.  These structures are basically big machines.
Miles of pipe, vessels, pumps, and other equipment all jam packed into half
the space it ought to occupy.  There are no walls, the upper level has
equipment on it exposed to the sky.  The challenge of laying out a sprinkler
system is often beyond imagination.  Eveyone is clamoring for every cubic
inch of space to put their stuff.  The red pipe, nobody thinks about that.

Just another day in paradise.   :)

Craig Prahl
CH2MHILL/SPB
864-599-4102


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to