The reservoir is elevated at around 50' higher than the pump centerline.
Suction head shouldn't be a issue.
There will be pendents without return bends, hence my suggestion for a y
strainer after the pump for the small particles.

Ed
Alpha Fire

On Fri, Jun 3, 2011 at 8:36 AM, Ronl.Fletcher <[email protected]>wrote:

> Would the strainer be a substitute for return bends on pendents?
>
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ed Cyr
> Sent: Friday, June 03, 2011 7:58 AM
> To: American Fire Sprinkler Association
> Subject: Centrifugal Horizontal Split Case Fire Pump - Intake Screens or In
> Line Strainer
>
> Forumites,
>
>
>
> I have used intake screens as prescribed by NFPA 20 in the past when
> drawing
> water for centrifugal fire pumps from a reservoir.
>
> Recently I have been asked to put in line strainers in the pump suction.
>
> Are they required when you have intake screens?
>
> The reservoir is being feed by a well. The reservoir is also lined with a
> membrane.
>
> My take is if any debris gets by the intake screens, it would be too small
> to damage the pump. A y strainer after the pump would filter any debris
> that
> might be detrimental to sprinkler performance.
>
> Any comments or suggestions would be appreciated.
>
> Thanks,
> Ed Cyr
>
> *Alpha Fire Sprinkler Corporation*
>
> *San Luis Obispo**, CA***
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to