Greg,
I'm not sure he's stating it correctly, but I think I understand what he's talking about.

DR-25 C900 pipe, when tested per AWWA C900-1997 standards, was given a pressure class of 100 psi.

The AWWA C900-2007 standards assign a pressure class of 165 to DR-25 pipe.

So, my thought is that we've been able to use DR-25 for some time, depending on the expected pressures in the underground portion of a private fire service main, of course. It is kind of interesting to note that the 1989 version of AWWA C900 was quoted in the 2007 edition of NFPA-24. That's been revised in the 2010, which references the 2007 edition of C900.

Insert NFPA-24 committee disclaimer here, as this is only my opinion, and doesn't represent anything but my own thoughts.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 6/6/2011 4:43 PM, Greg McGahan wrote:
I was told by a local AHJ that we can now use C900 DR-25 for fire mains
because of the new edition of the codes, does anyone know why?
Thanks,
Greg