Thanks for the reply. It looks like Mike's reference to 4.6.2.3.1 is
actually new to the 2010 ed. (being under sources in gen reqmnts) I was
wondering why my search in 2007 ed. only showed the exception to 150% in the
acceptance testing section and the backflow evaluation. But that is good
info to know.

What about where the city supply is capable of providing 150% but private
service main was undersized by the GC and will therefore not meet 150%
because of the friction losses solely in this portion of the line? Would it
be acceptable to settle for system demand or should a new line have to be
ran since technically the "source" (the city supply) is capable of the full
flow?



On Fri, Jun 10, 2011 at 5:29 AM, George Church <[email protected]>wrote:

Hmm, I'm not sure why meeting the system demand is a failure.
> So I have a site with a proposed building.
> City can meet demand, but not the 150%.
> You'd install a tank and pump while I bid pump.
> Good luck with that conservatism in the real world.
>
> Had a Come to Pelosi mtg yesterday with GC, Owner, and "giraffe" PE*.
> The PE allowed CPVC in nursing home BUT ONLY if owner gets a credit.
> So the PE has specified a system that meets code, but with steel pipe so
> the owner pays more than he should have to for it.
> That's is NOT being a good agent for the Owner.
> Again, ivory tower vrs contractor.
> Also, PE insists he has never heard an owner complain of overflowing a mop
> sink or 3" floor drain with a 2" main drain test.
> I asked if he'd ever personally witnessed a drain test like we were
> discussing. No, he hadn't.
> I told the owner I'd seen mop sinks overflow with ITC flow, 1/2" orifice,
> and we think a 2" main drain test isn't going to have water all over the
> floor?
> Again, people who have NO field experience advising an Owner what does and
> doesn't work.
> Ken pointed out that the PE wouldn't get the call from the owner.
> Their maintenance guy would call the GC who would call us and fix it.
>
> So now you know why I'm such a fan of design-build.
> The PE was fine with specifying 4" galv 40 threaded for the ATTIC
> sprinklers.... sure, that's a great installation with economy and long life,
> eh?
> Actually, this PE had specified the open wood truss attic to be protected
> by dry pendent sprinklers screwed into exposed piping in the attic.
> Hey, that is great fire protection. They cost more than ATTICs, they need
> to be tested every 10 years, and the deflector distance might be extended.
> How can you, when bidding, tell when the guy is wrong, or if he just wants
> somehtng really weird?
> The PE also routed the 4" supply thru an open breezeway, outside in PA.
> Duh...he didn't complain we fixed that routing.
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to