It seems part of the answer for your Client could hinge on a risk analysis.

1.  How important is the maintenance of business operations in other gas
cabinets
if one gas cabinet functionality is interrupted?
2.  How likely is it that an event which is capable of taking one gas
cabinet out-of-service
will occur?
3.  How likely is it that an event from item # 2, will also be capable of
taking other
gas cabinets O.o.S?
4.  What quantities of gas are involved?


Those types of "what-if" questions might give you some direction, if you
wanted to
customize the design beyond what prescriptions offer.   I know that
virtually all the
NFPA Standards allow for a performance based approach, which can save you
capitalized
and IT&M costs if the specific application you are designing to, warrants.
For example,
if the gases are flammable/explosive, and the facility is critical, your
Client's business
needs may be the driving force for going with redundant and separate
circuits.
If the gases in a particular cabinet are inert, it may not
be worth installing circuit separate from the other inerts.  If you need
flexibility
for future and unanticipated functionality, you may want separate circuits.