NFPA 22, 2008 

7.2.3.1 The water filling pipe shall be at least 1-1/2" in size, shall be run 
separately from the filling pump or other acceptable source of supply, and 
shall be adequately supported and protected from mechanical injury.

7.2.3.2 The filling pipe shall be connected to the top or bottom of the tank as 
required by the authority having jurisdiction. 

7.2.3.3 A listed horizontal bronze-seat swing check valve and a renewable seat 
globe valve shall be provided near the tank.

7.2.3.4 The globe valve shall be placed between the check valve and the tank.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, July 26, 2011 4:23 PM
To: [email protected]
Subject: tank fill line

As far as I can tell, the tank fill line doesn't have to be listed for fire
service. Can anybody confirm this?
Thanks,
Greg

-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to