The flash point is not determined on the MSDS and it is water miscible
stored in small glass bottles and its made out of 80% Ethyl Alcohol, 5%
water, 15% Costus oil and 2 % Trphrnyl tetrazolium chloride.  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, August 03, 2011 1:53 PM
To: [email protected]
Subject: RE: Perfume Storage

What is "highly flammable"?  That's not a classification.  What does the
MSDS say about flash point and boiling point of the materials?   The values
need to be specific.

Is the product miscible?

What kind of containers do they come in, glass, plastic, metal?  

Most perfumes that are classified as flammable end up being Class IB or IC
flammables due to some alcohol content.  

Be careful with the fire extinguishing methods in the MSDS.  They are geared
towards manual fire fighting means.  So if you walked up on a spill on fire
you wouldn't throw a bucket of water on it.  

Unless the MSDS clearly says do not put water on this chemical due to it
being reactive, sprinklers are not typically prohibited.  


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Wednesday, August 03, 2011 12:46 PM
To: [email protected]
Subject: Perfume Storage

I have a warehouse where they store highly flammable perfumes in small
bottles, the MSDS sheet states that they are highly flammable it also states
that fire extinguishing methods are co2, sand, powder and it says do not use
water. My question is does this mean that the sprinkler system has to be
taken out or is this for the portable fire extinguishers and the sprinkler
system gets designed as per NFPA 30 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to