FCNJ Section 905.2.2.1 Automatic water supply. An automatic water supply is
required for all standpipe systems. The automatic water supply and supply
piping shall be capable of delivering a flow of 500 GPM (1892 L/min) at the
residual pressure specified in Section 905.2.1 for a duration of 30 minutes.

 

 

Does the above section of the code apply to the pump size as well or is it
enough that underground service can handle it?

 

There is a section in the NJ IBC that allows to size the riser and feed main
for 1 standpipe @ 250GPM.

 

 