The 30 psi does include elevation and friction. My guess is that the inlet 
pressure of the pump would be around 16-18 psi. No, the pump house is part of 
the main structure and cannot be moved.


At 08:31 AM 8/24/2011, you wrote:
>Does the loss of 30 psi include the friction and the elevation loss? If not, 
>then you are getting pretty close to having cavitation at the pump inlet 
>and/or collapsing the supply pipe.
>
>Can you put the pump house lower on the hill?
>
>Matt Grisé PE*, LEED AP 
>Sales Engineer 
>Alliance Fire Protection 
>130 w 9th Ave.
>North Kansas City, MO 64116
>
>*Licensed in KS & MO 
>
>913.888.0647 ph 
>913.888.0618 f 
>913.927.0222 cell 
>www. AFPsprink.com 
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Wednesday, August 24, 2011 7:21 AM
>To: [email protected]
>Subject: Minimum pressures in water supply
>
>I am working on a new school project, where the building is 65 ft above the 
>water supply in the road and 760 ft horizontally. The water supply is 
>54-46-1130. There is a pump planned, which I have to size. The total pressure 
>loss in the underground between the supply and the pump house is approximately 
>30 psi. I know the general consensus (and some water company requirements) is 
>that the water pressure not be drawn down below 20 psi.  A 500 gpm at 60 psi 
>pump would be a good fit for this project, but the suction pressures at the 
>pump would end up being below 20 psi. The supply in the public mains would 
>remain above 20 (due to the elevation), but would be below that in the private 
>main at the pump room. Any thought if this would be acceptable?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to