Definitely not OH of any kind, I'm not even sure I'd go with EH1 owing to the 
potential depth of piles and chance for deep seated fires in Group A plastics 
and rubber.   Essentially you have a high piled storage situation with 
uncartoned, unstable piles.   

These types of facilities if using front-end loaders can pile materials 15-20 
ft high.   You should be looking towards CMSA Or ESFR's very carefully.

This is definitely not a pick-a-density from the chart type of project.

Craig P



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of å... ....
Sent: Wednesday, August 24, 2011 3:43 PM
To: [email protected]
Subject: Trash Recycling plant - Plastics, dust

As one approximation:
assume it is all seat cushions, expanded, uncartoned, exposed Group A
plastics solid piled to ____ (fill in your estimate here).

If there is more than an 1/8 inch of dust, no need to go out
and measure that 1/8th, just providing a rough picture for
coverage over areas exceeding the design area...then yes
the fire hazard warrants upping the design area.  However,
the warrant is issued by FM.   2010 NFPA 13 Section 5.4.1
says good to go with EH-1.

-- 
Scot Deal
Excelsior Fire


On Wed, Aug 24, 2011 at 6:36 PM, Art Tiroly <[email protected]> wrote:

>
> I am working on a proposed trash recycling plant. Automobile trash from a
> hammer mill type crusher arrives in  large dump trucks. All steel has been
> removed by magnets. This is mostly auto waste with a variety of
> combustibles: plastic, rubber, foam seats, carpeting, door panels, fiber
> board, wiring, etc. Non-ferrous metal will be recovered in this recycling
> system.
> The dust from the operation is combustible. The large piles of incoming and
> outgoing combustible waste in the shed is a concern.
> I think that with combustible materials drives this into Ex.HAZ. group 1
> and
> not OH2 and with larger areas of application.
> I am waiting for pictures from the pilot plant.
> Any thoughts and questions would be appreciated.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110824/0633ea14/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to