I just got my copy of the 2012 IBC yesterday.  Can't get any more current than 
next year!
 
Anyway, in that the definition of highrise is a building with an occupied floor 
more than 75' above the lowest level of fire department vehicle access (Chapter 
2).  The standpipe trigger is floor level of the highest story is more than 30' 
above the lowest level of fire department vehicle access.  Does not have to be 
occupied to trigger standpipes.  Commentary (I have the 2003) says this is 
based on how far the FD can pull a hose line into and up a building.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Thu, 8/25/11, George Church <[email protected]> wrote:


From: George Church <[email protected]>
Subject: RE: 75' Bldg Height
To: "[email protected]" <[email protected]>
Date: Thursday, August 25, 2011, 2:48 PM


I may have learned something!

I believe in the 2009 IBC, the word "occupied" is absent and so we're stuck 
with what could be higher levels of normally unoccupied space triggering 
high-rise requirements.
As I mentioned, either qualify your bid or have some documentation from AHJ 
that it is or isn't deemed high-rise.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of David de Vries
Sent: Thursday, August 25, 2011 2:28 PM
To: [email protected]
Subject: RE: 75' Bldg Height






George:
 
The highrise height trigger is based on the "lowest level of fd vehicle 
access".  So your outside stair would likely not trigger an added 15' to the 
building height.
 
Per IBC Commentary, 2003, for a highrise the 75' measurement is to the floor 
level of the highest occupied floor.  Whether a mechanical penthouse is 
considered to be "occupied" is a judgment call.  Note that "equipment spaces" 
frequented only be personnel for maintenace purposes, such as elevator 
penthouses and mechanical rooms are not required to be accessible to persons 
with physical disabilities (IBC 1103).  That language implies that such spaces 
are not considered occupied.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Thu, 8/25/11, George Church <[email protected]> wrote:


From: George Church <[email protected]>
Subject: RE: 75' Bldg Height
To: "[email protected]" <[email protected]>
Date: Thursday, August 25, 2011, 12:05 PM


If there is an outside stair down to a basement level, then that defines the 
lowest level of FD entry, so be careful.
Can add 15' to your elevation when starting a story below grade.
Wouldn't want to omit all the high-rise baggage!


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jeff Garrison
Sent: Thursday, August 25, 2011 12:28 PM
To: [email protected]
Subject: Re: 75' Bldg Height

Floor of highest occupied level to roadway or access elev..

Jeff Garrison
On Aug 25, 2011 12:06 PM, "Greg McGahan" <[email protected]> wrote:
> Question:
>
> When considering a building height for the purpose of determining
Automatic
> or Manual Standpipes in a building, is the height measured from the FD 
> access (asphalt or driveway adjacent to the building or portion of the
> building) to the FLOOR level of the highest occupiable level, OR the
overall
> building height?
>
> IS a Mechanical room on the roof considered and "Occupiable Level"
>
> Thanks,
> Greg
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: <
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110825/e311518a/attachment.html
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110825/0b55a03f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110825/96e6574e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110825/c4d8fceb/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to