I wouldn't consider this a canopy or porte-cochere but rather an extension of the horizontal exit or exit corridor. If you look at 8.15.7.4 the only allowance for omission of sprinklers in such exterior exit corridors is when the walls are 50% open. Doesn't sound like this exemption is met by this installation.
The architect would have to include this tube in his egress length calculations since you are not technically "out of the building" until you reach the end of the tube. Just at a quick glance it would sound like you may have to extend sprinklers the length of the tube. It will be interesting to see how the AHJ interprets this section of 13. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Thursday, September 15, 2011 10:06 AM To: [email protected] Subject: RE: Entrance/Exit Canopy?! Thank you - you actually walk through this tube to get to the front door of the office from the parking lot. It is attached to the building and self supported and sits on the ground. It has a flat walk in it that is about 5' to 6' wide. It looks like a piece of pipe that is sitting on its side on the ground and has settled in just enough to create a flat walk, if this makes any sense. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Gerald Schulhoff Sent: Thursday, September 15, 2011 8:39 AM To: [email protected] Subject: RE: Entrance/Exit Canopy?! If the tube is not suspended and open on the sides I do not think it will qualify as a canopy or porte-cochere.If the floor is flat and hard storage could be problem, even if you asked the local AHJ and get approval a change in reviewer can stop your project. Gerald Schulhoff SET Firewater Design(804) [email protected]> From: [email protected] > To: [email protected] > Subject: RE: Entrance/Exit Canopy?! > Date: Wed, 14 Sep 2011 16:29:32 -0500 > > I should have mentioned this facility is Production/Manufacturing with an > office. > > Thank you, Tom. > > Bobby Gillett > Sr. Project Manager > Key Fire Protection, Inc. > (731) 424-0130 office (731) 424-9285 fax > (731) 267-4853 cell > www.keyfireprotection.com > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Bobby Gillett > Sent: Wednesday, September 14, 2011 3:17 PM > To: [email protected] > Subject: Entrance/Exit Canopy?! > > I have a project I am bidding on that has an alternate for an entrance > "tube"; this is a non-combustible steel "tube" 30'-0 long and 16'-0 wide. > The beams are circular and are spaced horizontal to the building entrance > door/wall and the skin of the "tube" is perforated aluminum (perforation > size is unknown). Can I apply NFPA 13 2007 8.15.7.2 to this scenario? > > > > Thank you, > > > > Bobby Gillett > > Sr. Project Manager > > Key Fire Protection, Inc. > > (731) 424-0130 office (731) 424-9285 fax > > (731) 267-4853 cell > > <http://www.keyfireprotection.com> www.keyfireprotection.com > > > > > > > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20110914/e344340f/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > ----- > No virus found in this message. > Checked by AVG - www.avg.com > Version: 10.0.1392 / Virus Database: 1520/3896 - Release Date: 09/14/11 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20110915/6e22c0dd/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 10.0.1410 / Virus Database: 1520/3898 - Release Date: 09/15/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum