NFPA 101, Life Safety Code specifies the fire resistance rating required to enclose a vertical opening. See chapter 7, Means of Egress for stair enclosures. Without having it at hand, my recollection is that a stair connecting 3 or fewer floors needs one hour minimum. More than 3 floors needs two hour. I will check in the morning.
Dave On Wednesday, September 28, 2011, isam hboubate <[email protected]> wrote: > > Hi All, > Is there any regulatino in NFPA about use fire rated glass door in stair case. > Thanks, > Issam > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110928/d8870d5f/attachment.html > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110929/d9bdfdb8/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum