The water storage tank supplies the fire protection demand, either water required for the fire sprinkler demand or water to meet a fire flow requirement and sometimes both. There must be a source of water that will initially fill and then replenish the required amount of useable water within the tank in an 8 hour time period. There is nothing that I am aware of in the NFPA codes or the building codes that would require the pump supplying water the a storage tank to be listed for fire protection use or for that matter the materials used for the fill line to be listed either. Those components are not part of the fire protection system. The valve which maintains the level of water in the tank should be listed.
Byron Weisz Cen-Cal Fire Systems, Inc. 1615 So. Stockton St. Lodi, CA. 95240 Ph. (209) 334-9119 Fax (209) 334-2923 [email protected] This message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and/or confidential. If you are not the intended recipient any use, dissemination, distribution, or copying of this communication and attachments is strictly prohibited. Thank you. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Justin Reid Sent: Friday, October 07, 2011 6:56 AM To: [email protected] Subject: Re: Pump supplying water storage tanks As long as the tank is holding all of the demand water that is needed then it should not be required to be a fire pump. Justin Reid On Thu, Oct 6, 2011 at 6:45 PM, Sharon Alves <[email protected]> wrote: > Does a pump that supplies water from a well to water storage tanks need to > be a fire pump? > > > > Thank you, > > > > SHARON ALVES > > Senior Fire Sprinkler Designer > > > > LP Consulting Engineers, Inc. > > Mechanical - Electrical - Plumbing Engineers - Fire Protection > > 1663 Eureka Road > > Roseville, CA 95661 > > P: 916.771.0778 - F: 916.783.9446 > > [email protected] > > > > This email and its attachments are the sole property of LP Consulting > Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2010. > This > communication with its contents may contain confidential and/or legally > privileged information. It is solely for the use of the intended > recipient(s). Unauthorized interception, review, use or disclosure is > prohibited and may violate applicable laws including the Electronic > Communications Privacy Act. If you are not the intended recipient, please > contact the sender and destroy all copies of the communication. The sender > and its company do not guarantee that this email or its attachments is free > of viruses nor does it accept any liability for same > > > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments /20111006/eb6cb940/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20111007/ac7725e8/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum