It would probably be a performance based design. I can't remember seeing 
anything in NFPA but I have seen videos of spherical tank systems being tested.

Here is an excerpt from Fire Engineering Magazine, I don't have the issue or 
date.

"The first method involves the use of a water deluge system and some form of 
water distributor. This could include high-volume spray heads, perforated pipe, 
or a distribution weir. An underflow or overflow weir allows water to be evenly 
distributed over the surface area of a sphere; water flows up the piping 
network, over the top of the sphere, and out of the weir. This type of water 
distributor is commonly used but is prone to corrosion from standing water and 
clogging and requires increased preventative maintenance. Additionally, weirs 
may not be as effective on bullets and are often greatly affected by wind. The 
remaining components of this method are similar to other deluge installations. 
The typical deluge system contains a supply piping network, deluge valve and 
trim, and branchline-piping network near the top of the sphere. Newer 
installations are usually activated automatically, whereas older installations 
are commonly activated manually. The decision of which activation method to use 
requires evaluation of spacing, available protection, exposures, and other 
factors.

The principle behind the deluge or weir system for LPG sphere protection is 
that the geometric shape of the sphere and gravity work together as an 
advantage. As water is applied to the top of the vessel, the shape of the 
sphere and the force of gravity facilitate the flow of the water as it covers 
the surface area of the vessel. This type of protection is very effective to 
facilitate an even distribution of water over the surface area. Caution should 
be exercised, however, because paint, corrosion, dust, and other environmental 
influences can cause changes in the surface of the sphere, resulting in uneven 
water distribution. Additionally, settling and other conditions inside the weir 
can also cause uneven water flow over the sphere's surface."


Ron Fletcher
Aero Automatic
Phoenix, AZ



 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Wednesday, October 12, 2011 7:40 AM
To: [email protected]
Subject: RE: Top Spray Deluge nozzle

Can you point to anything in NFPA that will allow this design application? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd Rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Tuesday, October 11, 2011 1:25 PM
To: [email protected]
Subject: RE: Top Spray Deluge nozzle

I'm looking for a nozzle with a 1½" up to 3" discharge orifice.  I think it
is something a local shop would have to fab up.  Thanks though.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-3662

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Tuesday, October 11, 2011 12:20 PM
To: [email protected]
Subject: Re: Top Spray Deluge nozzle

Tyco still manufactures what was the Grinnell EA-1, although I don't know if
they still call it that, which comes in various configurations of spray
pattern.


On Tue, Oct 11, 2011 at 9:59 AM, Hinson, Ryan <[email protected]> wrote:

> Does anyone out there know of a manufacturer of top spray deluge 
> nozzles which basically flow water at the top of storage spheres for 
> rundown over the entire storage vessel?  I have a client standard 
> detailing what they are looking for but cannot locate anything online.
>
> Thank you,
>
> Ryan L. Hinson, EIT, SET
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns & 
> McDonnell Minneapolis-St. Paul Office
> 8201 Norman Center Drive, Suite 300
> Bloomington, MN 55437
> Direct: 952-656-3662
> Fax: 952-229-2923
> [email protected]
> www.burnsmcd.com<BLOCKED::www.burnsmcd.com>
>
>
> Proud recipient of PSMJ's Premier Award for Client Satisfaction
>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hments/20111011/5f47e1b9/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111011/d4069ef9/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to