22.4.1.2 Pipe sizes shall be no less than 1 in. (25 mm) nominal
for ferrous piping and 3⁄4 in. (20 mm) nominal for copper
tubing or nonmetallic piping listed for fire sprinkler service.

2010 EDITION

On 10/20/2011 9:49 AM, George Medina Jr wrote:
Forum,

I surveyed a high rise in Los Angeles for a tenant improvement and the entire system 
was done in Copper. I noticed the drops and end of lines were in 3/4" copper. 
Is that allowed in NFPA-13? The system is not more than 25 years old. If it is 
allowed, can somebody point me to the code section.

Thank,
George Medina Jr.