In a water or antifreeze filled wet system (in service long enough to
completely absorb all air) and the common practice of using backflow
preventers, a system subjected to high temperature swings will could
experience high pressures that cannot be dissipated thru a 1/32" hole in a
clapper of the check valve.  Hence escalating pressures and no way to vent
same.  Pressure chamber does the trick.

John O'Connor
Nashville TN
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Wednesday, October 26, 2011 2:13 PM
To: [email protected]
Subject: Expansion chamber for anti-freeze

Can anybody explain why I would need an expansion chamber for an anti-freeze
system when there is only 60 psi in the street?

 

NFPA does not make a difference for low street pressure.

 